Hello ,
We are using CY8CPLC20 controller for power line communication (PSOC1) . "FSK modem only " is selected .Example code given in the datasheet is flashed on both the kits. In the receive end before receiving the data some garbage values are received. suppose i send (AB, 01,10,23,88..) , at the receive end i get values like (FF,FF,FF,FF,AB,FF,FE,FF,FF,FF,FF,FF,10,FF,FF......). Do i need to append overheads to the transmit message?
Regards,
Divya K
Solved! Go to Solution.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
Hello Divya,
1) Kindly refer to page 8 and page 9 of PLT v 1.50 datasheet.
2) The powerline used for communication may be noisy.
The receiver gain may be too high
Noise level threshold may be low
3) You can kindly refer to PLT v 1.50 datasheet. The Sample codes are in pages 41 and 42. Unfortunately, we do not have a seperate document for Modem Only.
Best regards,
Sampath
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
Hello Divya,
You will have to use the same Network Packet structure, as shown in the datasheet of PLT User Module.
Best regards,
Sampath
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
Hi Sampath,
1]can you tell which page no. of PLT user module you are suggesting?
2] Even if you don't send anything(disconnect one controller) ,we are receiving some garbage values( FF ,FB ...)
why is it so?
3] can you provide any detailed document for implementing PLT using FSK modem only.?
Regards,
Divya K
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
Hello Divya,
1) Kindly refer to page 8 and page 9 of PLT v 1.50 datasheet.
2) The powerline used for communication may be noisy.
The receiver gain may be too high
Noise level threshold may be low
3) You can kindly refer to PLT v 1.50 datasheet. The Sample codes are in pages 41 and 42. Unfortunately, we do not have a seperate document for Modem Only.
Best regards,
Sampath