PSoC™ 4

David_Zhang
New Contributor II

      customer feedback  false trigger issue when the temperatures change  dramatically such as the car was in the sun for  serval hours, it will be high temperature in the car,

and now we open air conditioner , the temperature will slow down from high to low fastly, the fales triggering issue occur. i find blow the function in capsense v3.0 higher;

when custoemr used capsense v2.0, how we help customer to set IDAC,  capsense v2.0 has no place to set value. show in figure2, below:

Figure 1 pastedImage_0.png

Figure2

pastedImage_7.png

0 Likes
1 Solution
4 Replies
RyanZhao
Moderator
Moderator

Hi David,

if the temperature pulled down to a low level by AC, the baseline may fall fast and trigger low baseline reset. But if the temperature can be stable at the low level, rawcount and baseline should be similar and won't cause false trigger, unless there are more complex environment factor change.

Recommend to share with us the project and dynamic rawcount and baseline tuner data when the issue happened which will can help us to analyze it better.

If the project is customer confidential, suggest to create an SFDC case for further discussing and tracking.

No matter CapSense_CSD 3.x/4.x/5.x or CapSense_CSD 2.0, if IDAC auto-calibration is checked, IDAC will not be able to be changed by users.

In CapSense_CSD 2.0, unchecked Auto-calibration, you can tune IDAC at the place shown in the below picture.

pastedImage_2.png

Thanks,

Ryan

0 Likes
David_Zhang
New Contributor II

Dear Ryan:

     how do i choose the value of Modulation IDAC and Compensation  IDAC, if you have the instructions fies for it? thanks

0 Likes
David_Zhang
New Contributor II

The project is belo

0 Likes