I have made user UART communication between General MCU and imc101t. I can control the motor using the write register command. in my MCU uart program, I judged that the communication with imc101t was interrupted, I reinitialized my UART, but I still can't communicate with IMC101T. After power on again, the communication returns to normal.
Because the product is in the customer's place, I can only see that the parameters of imc101t are not updated through the HMI. Moreover, the communication interruption is an accidental event, and I can not judge whether it is the problem of MCU or the problem of imc101t.
how can I solve the communication failure? How does imc101t handle link break ?
Solved! Go to Solution.
- Tags:
- imotion
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
Hi @yangyong,
If the UART Link break fault is triggered then the motor goes into a fault state and the motor stops.
This fault occurrence can be detected by reading the register FaultFlags (bit 13) using the script.
For more details refer to section 3.2.8.15 FaultFlags iMOTION – MCE – Software Reference Manual v1.3
Please write a custom script to detect this fault and this fault can be cleared by writing 1 to FaultFlags this will reset the fault condition and initialize the UART lines.
For more details regarding script please refer to : How to Use iMOTION™ Script Language
Please let us know if any further details are required.
Thanks,
Krupashankar
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
Hi @yangyong ,
UART Link Break fault can be enabled to detect communication failure, fault is triggered if there is no communication in the UART line for the specified break out time.
- UART Link break fault can be enabled by setting the parameter FaultEnable bit [13] to 1 to enable link break fault (add 8192 to existing FaultEnable value) parameter.txt file. This particular fault has to be cleared with user script.
- UART link break time to trigger fault can be changed by varying UART1_LinkBreakCount in the parameter.txt file ( UART1_LinkBreakCount each count is 1mSec ).
If UART Link break fault is triggered then motor goes into fault state and it can be cleared by writing 1 to FaultClear using script. This helps to detect the communication failure and restore the fault.
Please design your application using this fault.
Thanks,
Krupashankar
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
If UART Link break fault is triggered, It means that the communication between MCU and imotion is collapses. iMotion may not receive FaultClear command. i mean, when imotion detects UART LINK FAULT, what will it do? Will it initilize the UART to restore the UART to normal.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
Hi @yangyong,
If the UART Link break fault is triggered then the motor goes into a fault state and the motor stops.
This fault occurrence can be detected by reading the register FaultFlags (bit 13) using the script.
For more details refer to section 3.2.8.15 FaultFlags iMOTION – MCE – Software Reference Manual v1.3
Please write a custom script to detect this fault and this fault can be cleared by writing 1 to FaultFlags this will reset the fault condition and initialize the UART lines.
For more details regarding script please refer to : How to Use iMOTION™ Script Language
Please let us know if any further details are required.
Thanks,
Krupashankar