IMC101T-F048 with IM535 Give Error 128

Announcements

From sunburn to sun earn – we’ve got the power! Watch our #poweringgreen videos now.

Tip / Sign in to post questions, reply, level up, and achieve exciting badges. Know more

cross mob
sohail
Level 3
Level 3
50 sign-ins 10 questions asked 10 replies posted

Hi @LinGuohui 

                                   when I Run Motor with full Load it was Running for few Moments. Then is start Giving Error  Flag 128.

I check User manual but fault Flag Available in Range 0-15. 

 

Error_flag.png

Flag Description.png

 

Can you pl help what is this Fault Flag 128.

Thanks 

0 Likes
1 Solution
LinGuohui
Moderator
Moderator
Moderator
500 replies posted 50 likes received 250 solutions authored

Hi @sohail 

Flag 128, it is Rotor Lock Fault. You can refer MCESW-RM-UserManual-v01_03  chapter 2.1.16.2

LinGuohui_0-1663552460761.png

Rotor lock fault is detected if the speed PI regulator output (variable‘TrqRef’) is being saturated for a defined amount of time 𝑇𝑅𝑜𝑡𝑜𝑟_𝐿𝑜𝑐𝑘. T

Rotor Lock Fault is active when the motor speed ranges from min motor speedto 25% of maximum speed.inactive when the motor speed goes beyond 25% of maximum speed. 

Therefore, This fault is because you give full Load with low speed (<25% max speed).

 

View solution in original post

0 Likes
1 Reply
LinGuohui
Moderator
Moderator
Moderator
500 replies posted 50 likes received 250 solutions authored

Hi @sohail 

Flag 128, it is Rotor Lock Fault. You can refer MCESW-RM-UserManual-v01_03  chapter 2.1.16.2

LinGuohui_0-1663552460761.png

Rotor lock fault is detected if the speed PI regulator output (variable‘TrqRef’) is being saturated for a defined amount of time 𝑇𝑅𝑜𝑡𝑜𝑟_𝐿𝑜𝑐𝑘. T

Rotor Lock Fault is active when the motor speed ranges from min motor speedto 25% of maximum speed.inactive when the motor speed goes beyond 25% of maximum speed. 

Therefore, This fault is because you give full Load with low speed (<25% max speed).

 