Hello, trying to drive a refrigeration compressor with CTE620N3 and IMC101T-F048 boards.
The program might be wrong since when starting the motor I just hear a small click and the "motor fault" message on MCEDesigner.
Tried everything on MCEDesigner to get at least a fault code but no results, is there a way to know which fault is it ?
Thanks in advance.
Solved! Go to Solution.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
Hi @Airtech,
About "motor fault" message, You can use MCEDesigner to read Faultflags register to know which fault it is.
Operation steps see below:
a) Get register message on user manual, mark its address, data type and every bit represent fault.
b) Add this register read on MCEDesigner , input its address and Unsigned type.
c) And then, you can read this faultflags via double click this register. So you will get which fault is it!
Below picture,Faultflags read 8192, we can know it's UART link break fault.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
Hi @Airtech,
About "motor fault" message, You can use MCEDesigner to read Faultflags register to know which fault it is.
Operation steps see below:
a) Get register message on user manual, mark its address, data type and every bit represent fault.
b) Add this register read on MCEDesigner , input its address and Unsigned type.
c) And then, you can read this faultflags via double click this register. So you will get which fault is it!
Below picture,Faultflags read 8192, we can know it's UART link break fault.